The location suffered a tube perforation in the convection bank due to sulphur corrosion. The combination of the use of carbon steel with the use of a sulphur containing hot oil medium and the fact that the hot oil system was being operated at high furnace outlet temperatures was responsible for the corrosion. The increase in the temperature of the flue gas entering the convection bank will have increased the severity of the corrosion, leading to the perforation occurring earlier than would
Otherwise have been the case.
The second location suffered tube failures in the first layer of finned convection bank tubes, where apparently the heat flux (based on bare tube area) was higher than on the bare shock tubes. Higher heat flux results in higher film temperatures inside the tube.
Both these incidents followed an incident two years earlier which resulted in a change in the furnace DEP (DEP.31.24.00.30-Gen October 1995) to a recommended maximum film temperature in hot oil systems furnace/convection bank tubes (previously a maximum bulk outlet temperature had been specified). In both the latest and earlier incidents, fires occurred in the convection bank during the shutdown process.
The learning points are as follows:-
When considering a change to 100% gas firing remember to take into consideration the resultant increased temperature of the flue gas entering the convection bank. This is especially important if the convection bank is fabricated from carbon steel and/or the hot oil fluid contains sulphur. For carbon steel tubes, the film temperature in the convection bank should be kept below 330°C. Recognising that most locations do not measure film temperature (or even shock tube skin temperature) it is recommended that
where there are carbon steel tubes in the upper section of the convection bank, the outlet temperature of every furnace coil should be kept below 320 deg.C. Monitoring of the hot oil fluid flash point is a means to identify degradation of hot oil fluid - this can be taken as an indicator of excessive temperatures within the furnace. It should also be noted that the presence of light material can mean that vaporisation takes place within the furnace tubes which can lead to tube rupture due to localised overheating.
Consideration should be given to the use of 5Cr½Mo tubes in place of carbon steel in the upper sections of the convection bank, if the hot oil fluid contains sulphur, when replacing tubes or when considering a change in furnace firing mode. All incidents occurred on relatively old furnaces. After a long period of operation some more detailed inspection may be required to ensure that locations where slow corrosion rates are occurring are checked. In addition to the shock tubes, inspection should then focus on places with surface extensions, such as spacer strips and the first row of finned tubes.
Provided that the perforation of the convection bank is not major, the first sign of a problem is usually a change in the colour of the stack. This becomes yellow/brown due to the presence of uncombusted material. In the event of several furnaces sharing a stack it is not always easy to identify the culprit. One technique which may be useful is to see if the convection bank outlet temperature is significantly different from normal - it will be higher in the event of combustion in the convection bank.
Perforation of a radiant cell or convection bank tube will necessitate shutting down of the hot oil system in order to effect a repair. The recommendation from the location that suffered the latest incident is to shutdown immediately after a leak is identified.
The shutdown procedure is not without risks - one location burnt down their furnace as a result of a flawed shutdown procedure which resulted in a severe fire within the convection bank. It is not possible to give a single standard procedure since four cases have to be considered; small radiant cell leak, large radiant cell leak, small convection bank leak and large convection bank leak. Furthermore the presence of other furnaces using the same stack can affect the choice of procedures. Thus each refinery should, if they have not already, develop procedures (and practice them!) for dealing with leaks in the hot oil furnace.
The following points will help in the development of such procedure:
With the exception of very minor leakages, care should be taken to keep oxygen levels as low as possible to minimise the risk of combustion or explosion in the convection bank or stack system. In the case of minor leakages the air flows should be increased to maximum once the furnace is stopped. In this way the air/hydrocarbon mixture in the convection bank is kept below the lower explosion limit. In case of doubt about the size of leak, ingress of air should be minimised (by stopping blowers and introducing smothering steam) in order to stay above the upper explosion limit during the cool down period. Where several furnaces share a common stack, all the furnaces connected to the stack should be operated at
Minimum oxygen levels. If possible hydrocarbons should be evacuated from the affected coil by injecting steam, whilst the fires are still lit in the furnace. It may be necessary to use the maintenance override to prevent the low coil flow trip from shutting off the fuel supply. Introducing steam into the coil shall be done gently, to prevent pressure surges which could lead to tube ruptures. Never steam out a coil in a hot furnace unless either air flow is stopped or burners are lit - this recommendation is made to avoid
excessive oxygen being present when there is a risk of leaking material igniting.
------------------------------------
88.I: FURNACE TUBE BURST
Summary
During a statutory shutdown of a chemical plant, a heating system operating on santotherm heating fluid, and consisting of a circulation grid over various units and a heating furnace, was partly drained off. Upon restart, cracks developed in three of the twelve vertical heating coils in the radiant section. This resulted in santotherm leaking and burning in this section. While measures were being taken to remedy the situation, a complete tube burst of a fourth coil occurred. The suddenly increased outflow of
santotherm was partly transferred to the 100 m high furnace stack. For about 10 minutes an approximately 30 m high flame emerged from the top of the stack, accompanied by a large cloud of soot. This soot was carried away and deposited over populated areas several kilometres away from the site.
Public and press reacted with irritation to the event. Repair work on the furnace postponed the start-up by approximately three weeks.
The furnace
A circulation pump feeds the heating liquid to the furnace. In the radiant section the santotherm flows through 12 vertical radiant coils, of 12.30 m length. The coils have 6 vertical hairpins. Near the furnace roof the outlets are combined to 1 header. Each coil is provided with a temperature measuring point on the outlet side which is scanned every three minutes. Measured values are stored. Burners are mounted in the furnace floor.
The radiant coils form a completely open parallel system. There are no individual block valves on the coils, nor flow indicators. During normal operation 1250 tons/hr of santotherm is circulated and heated up to approximately 340*c. Inlet pressure is approximately 12 barg and the pressure drop under full flow conditions is approximately 2 bar; design pressure drop over the radiant coils only is 0.6 bar.
Some characteristics of santotherm are : flash point 178*C, auto-ignition at 390*C, boiling point over 450* C. It starts cracking with carbon formation above 400*C. Design skin temperature of the radiant coils is below400*C. Carbonization with creep and cracking starts at 500*C. |
|